The relay interprets a mismatch between the currents measured at the boundaries of a protected section as evidence that the normal through-current relationship has been disturbed. Current transformers provide the measurements on each side, while a set operating threshold determines whether the mismatch is large enough to initiate protection action. This comparison supports selective isolation of the affected section.
Restraining features improve stability by reducing the likelihood of unwanted operation when the protected equipment is not experiencing an internal fault. They are especially important during external faults, transformer inrush, and current-transformer errors, all of which can produce misleading current differences. This restraint allows the relay to remain dependable while preserving sensitivity to genuine internal faults.
The protected section establishes which conductors and equipment the relay evaluates as one electrical zone. Current transformers must measure the conductors at the relevant boundaries so the comparison corresponds to that section. When the measured difference exceeds the selected threshold, the relay can identify a fault within the intended zone rather than responding to conditions outside the protected equipment.
A typical scheme first defines the electrical section requiring protection, then places current transformers on the conductors at its boundaries. The relay receives the transformer measurements, compares the currents entering and leaving the section, and evaluates the difference against a set threshold. Restraining features may then help determine whether the condition represents an internal fault or a disturbance.
Differential protection is applied to power transformers, generators, motors, and busbars. These assets can be assigned defined protection sections with current measurements at their boundaries, allowing faults within the equipment to be distinguished from conditions elsewhere in the network. Applying the method across these assets supports targeted fault isolation rather than unnecessarily disturbing unaffected parts of the system.
By responding selectively to faults associated with the protected section, differential relays can support fast isolation of the affected equipment. This action helps limit equipment damage and contributes to the reliability and stability of the wider electrical network. Their value is greatest where rapid fault clearing must be combined with discrimination between protected equipment and external system conditions.